<div dir="ltr">Hi Dave,<div><br></div><div>Sorry for adding to the confusion. The fridges, freezers and autoclave I talked about are for Counter Culture Labs (CCL), on the other side of the hall from Sudo Room. The diagrams you've seen are for Sudo Room - we haven't come up with a wiring diagram for CCL yet (and we could use some help with that!) Other than the robot arm, Sudo will likely use quite a bit less power than CCL. </div><div><br></div><div>Patrik</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Sat, Sep 6, 2014 at 4:01 PM, Dave Pedroli <span dir="ltr"><<a href="mailto:davepedroli@gmail.com" target="_blank">davepedroli@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi all,<br>
<br>
Going over your emails and PDFs it looks good however putting more than a couple outlets on a breaker will end up being problematic.  Yes refrigerators are smaller loads but there will be a time when someone opens all one after the other and they try to start all at once blowing a breaker and defrosting... Autoclaves typically need their own circuit etc ...  13 outlets with 4 breakers is pushing it. If the majority of use was to be laptops and soldering irons ok but the minute a heat gun is plugged in poof, you blow a breaker. With electricity and parachutes it's best to start out right rather than build up to it.  I'll go over the PDFs on my iPad later and let you know what I think.  The layout looks fine, the number of outlets looks good it's just the the number of circuits (breakets) that needs improving.<br>
<br>
<br>
Dave<br>
<br>
Somewhere on the bonneville salt flats<br>
<br>
<br>
Sent from the surveillance van<br>
<div class="HOEnZb"><div class="h5"><br>
> On Sep 5, 2014, at 3:58 PM, Jake <<a href="mailto:jake@spaz.org">jake@spaz.org</a>> wrote:<br>
><br>
> I believe the electrical panel in the balcony only supplies one or two things (not including the robot, which is a temporary connection)<br>
><br>
> I think we should look into simply moving that breaker box down ten feet so it faces the server room, and be done with it.<br>
><br>
>> On Fri, 5 Sep 2014, Whitney Lawrence wrote:<br>
>><br>
>> Howdy,Let me begin with thanking you for looking at the proposal. Your interpretation of the plans is<br>
>> correct.{ Main -> above stage panel -> balcony panel } is how the proposed plan is drawn. There is enough room<br>
>> in the balcony panel (which is the one located in the small room that shares a wall with the server loft of<br>
>> sudoroom) to accomplish phase 1 of the proposal. The proposal is based on instruction received to minimize<br>
>> cost. Ideally, there would be a main panel breaker that supplies a sub panel for all of sudo's needs (phase 1<br>
>> and phase 2). I can't accurately guess at a cost number for this type of installation. Figure a 100amp sub<br>
>> with hundreds of feet of 2awg plus breaker box plus breakers plus conduit plus hardware. All depending on if<br>
>> the main service can even handle the additional power demands (hiring an electrician to run the calcs).<br>
>> Ballpark $3-5k maybe- but its really a shot in the dark?<br>
>> My experience with this type of thing is there is always a better way to do it, if you go the money.<br>
>> A middle road is to plan on having the future sudo-sub panel placed near the balcony panel. Build in an extra<br>
>> 5ft or so of wire for the future transition into the new sudo-sub panel. All that would be needed is to remove<br>
>> the breakers from the old box re-run wire from J-box 1 to the new sudo-sub, as well as re-routing the 240V<br>
>> lines from the above stage panel to the sudo-sub (and of course preform all the main -> suod-sub work).<br>
>> as far as existing vs proposed. only the sub panels mentioned above exist currently- I'll make a note to call<br>
>> out the existing stuff in the drawings.<br>
>> Thanks,<br>
>> Whit<br>
>> On Fri, Sep 5, 2014 at 11:42 AM, Cere Mona Davis <<a href="mailto:ceremona@gmail.com">ceremona@gmail.com</a>> wrote:<br>
>>      Hi everyone.  It's the first time I have looked at these plans and I have some questions and<br>
>>      thoughts.  Dave said he won't be able to respond to this email until a couple of days as he is out<br>
>>      in the boonies somewhere.  So I am writing in to expedite some issues that I think he will likely<br>
>>      bring up in the days ahead.<br>
>> Whit, thanks for drawing up these plans!  For someone who is not intimately familiar with our electrical<br>
>> layout the plans might need a more clear description of existing electrical vs. proposed new electrical,<br>
>> however.<br>
>> In multiple conversations with Dave (and one on-site visit) he has mentioned repeatedly that we will<br>
>> want to shoot for putting in another sub panel for the sudoroom off of the main panel as the end-game;<br>
>> rather than daisy-chaining off of an existing panel (the balcony) as what seems to be proposed here.<br>
>> If we can't immediately put in a sub panel into the room, due to cost, we should at-least be planning<br>
>> for conduit and wiring paths, etc that allows for a sudoroom sub-panel in the future.<br>
>> Thoughts?<br>
>> -Cere<br>
>><br>
>> On Fri, Sep 5, 2014 at 10:23 AM, <<a href="mailto:hol@gaskill.com">hol@gaskill.com</a>> wrote:<br>
>><br>
>>      Thanks Yar!  Whit can you liaise w/ Dave RE how much of the work is going to be done under<br>
>>      the first permit?<br>
>><br>
>><br>
>><br>
>>      Cheers,<br>
>><br>
>>      Hol<br>
>><br>
>><br>
>><br>
>><br>
>> On 2014-09-04 23:16, yar wrote:<br>
>> Hi all, Dave Pedroli is a certified electrician who's offered to<br>
>> review our plans to give them an okay. I'm copying him and the people<br>
>> who've been most involved with electrical work.<br>
>> Dave, the latest plans are attached, and also available online[1].<br>
>> Could you please look them over and write us a few formal-sounding<br>
>> sentences that boil down to "hello I am a real electrician and I say<br>
>> these plans are solid"? This will help us make the landlord happy so<br>
>> he will let us do them. Thank you!!<br>
>> [1] <a href="https://lists.sudoroom.org/pipermail/sudo-discuss/2014-August/007369.html" target="_blank">https://lists.sudoroom.org/pipermail/sudo-discuss/2014-August/007369.html</a><br>
>> --<br>
>> Best Regards,<br>
>> Cere Davis<br>
>> <a href="mailto:ceremona@gmail.com">ceremona@gmail.com</a><br>
>> -------------------<br>
>> GPG Key:  <a href="http://taffy.findpage.com/~cere/pubkey.asc" target="_blank">http://taffy.findpage.com/~cere/pubkey.asc</a><br>
>> GPG fingerprint (ID# 73FCA9E6) : F5C7 627B ECBE C735 117B  2278 9A95 4C88 73FC A9E6<br>
</div></div><div class="HOEnZb"><div class="h5">_______________________________________________<br>
sudo-discuss mailing list<br>
<a href="mailto:sudo-discuss@lists.sudoroom.org">sudo-discuss@lists.sudoroom.org</a><br>
<a href="https://lists.sudoroom.org/listinfo/sudo-discuss" target="_blank">https://lists.sudoroom.org/listinfo/sudo-discuss</a><br>
</div></div></blockquote></div><br></div>