In picture 3 is a box with knockouts being used for portable power
distribution. This is the incorrect type of box for this function. These
boxes are for permanent mounting. Additionally, the strain relief is for
romex type cable, a gland type cable grip should be used for SEOOW cable.

In picture 5, there is inappropriate use of what looks like MC cable.